Time adjusted rule for orifice setting
I want to control opening and closing of an orifice depending on the flow in a downstream link. I want to close the orifice for 15min if the flow in the d/s exceeds say 50 LPS, after 15 min I want to check again the flow in the link and adjust the opening-closing of the orifice depending on the flow above-below 50LPS. How can I writet a rule which can solve this problem?
  • [TITLE]
    ;;Project Title/Notes
    [OPTIONS]
    ;;Option Value
    FLOW_UNITS CFS
    INFILTRATION GREEN_AMPT
    FLOW_ROUTING DYNWAVE
    LINK_OFFSETS ELEVATION
    MIN_SLOPE 0
    ALLOW_PONDING NO
    SKIP_STEADY_STATE NO
    START_DATE 01/01/1988
    START_TIME 00:00:00
    REPORT_START_DATE 01/01/1988
    REPORT_START_TIME 00:00:00
    END_DATE 01/01/1988
    END_TIME 06:00:00
    SWEEP_START 01/01
    SWEEP_END 12/31
    DRY_DAYS 0
    REPORT_STEP 00:01:00
    WET_STEP 00:15:00
    DRY_STEP 01:00:00
    ROUTING_STEP 0:00:10
    INERTIAL_DAMPING NONE
    NORMAL_FLOW_LIMITED BOTH
    FORCE_MAIN_EQUATION H-W
    VARIABLE_STEP 0.75
    LENGTHENING_STEP 10
    MIN_SURFAREA 12.566
    MAX_TRIALS 8
    HEAD_TOLERANCE 0.005
    SYS_FLOW_TOL 5
    LAT_FLOW_TOL 5
    [EVAPORATION]
    ;;Evap Data Parameters
    CONSTANT 0.6
    DRY_ONLY NO
    [JUNCTIONS]
    ;;Junction Invert MaxDepth InitDepth SurDepth Aponded
    10309 101.60 9.40 .00 0 0
    10309a 101.60 9.40 .00 0 0
    10309b 101.60 9.40 .00 0 0
    10309c 101.60 9.40 .00 0 0
    10309d 101.60 9.40 .00 0 0
    10309e 101.60 9.40 .00 0 0
    15009 111.50 13.50 .00 0 0
    15009a 111.50 13.50 .00 0 0
    15009b 111.50 13.50 .00 0 0
    15009c 111.50 13.50 .00 0 0
    15009d 111.50 13.50 .00 0 0
    15009e 121 13.50 .00 0 0
    16009 102.00 18.00 .00 0 0
    16009a 102.00 18.00 .00 0 0
    16009b 102.00 18.00 .00 0 0
    16009c 102.00 18.00 .00 0 0
    16009d 102.00 18.00 .00 0 0
    16009e 102.00 18.00 .00 0 0
    16109 102.80 22.20 .00 0 0
    16109a 102.80 22.20 .00 0 0
    16109b 102.80 22.20 .00 0 0
    16109c 102.80 22.20 .00 0 0
    16109d 102.80 22.20 .00 0 0
    16109e 102.80 22.20 .00 0 0
    ;JUNCTION DATA
    80408 120 13.40 .00 0 0
    ;2nd network or extran example 2
    80408a 124.60 13.40 .00 0 0
    ;3rd network or extran example 3
    80408b 124.60 13.40 .00 0 0
    ;4th network or extran example 4
    80408c 124.60 13.40 .00 0 0
    ;5th network or extran example 5
    80408d 124.60 13.40 .00 0 0
    ;6th network or extran example 7
    80408e 124.60 13.40 .00 0 0
    80608 118.30 16.70 .00 0 0
    80608a 118.30 16.70 .00 0 0
    80608b 118.30 16.70 .00 0 0
    80608c 118.30 16.70 .00 0 0
    80608d 118.30 16.70 .00 0 0
    80608e 118.30 16.70 .00 0 0
    81009 128.20 8.80 .00 0 0
    81009a 128.20 8.80 .00 0 0
    81009b 128.20 8.80 .00 0 0
    81009c 128.20 8.80 .00 0 0
    81009d 128.20 8.80 .00 0 0
    81009e 128.20 8.80 .00 0 0
    81309 117.50 12.50 .00 0 0
    81309a 117.50 12.50 .00 0 0
    81309b 117.50 12.50 .00 0 0
    81309c 117.50 12.50 .00 0 0
    81309d 117.50 12.50 .00 0 0
    81309e 117.50 12.50 .00 0 0
    82308d 112.30 42.70 .00 0 0
    82309 112.30 42.70 .00 0 0
    82309a 112.30 42.70 .00 0 0
    82309b 112.30 42.70 .00 0 0
    82309c 112.30 42.70 .00 0 0
    WetWell 112.30 21 .00 0 0
    [OUTFALLS]
    ;;Outfall Invert Type Stage Data Gated
    10208 89.9 FREE NO
    10208b 89.9 FREE NO
    10208c 89.9 FREE NO
    10208d 89.9 FREE NO
    10208e 89.9 FREE NO
    10208a 89.9 FIXED 94.4 YES
    [STORAGE]
    ;;Storage Node Invert MaxDepth InitDepth Shape Curve Name/Params Fevap Seepage
    ;* STORAGE JUNCTION AT JUNCTION 82309d for the 5th network
    82309d 112.3 42.7 0.0 FUNCTIONAL 800.0 0 0 0 0
    [CONDUITS]
    ;;Conduit From Node To Node Length Roughness InOffset OutOffset InitFlow MaxFlow
    1030e 10309e 10208e 4500.0 0.016 * * 0.0 0
    1030 10309 10208 4500.0 .20 * * 0.0 0
    1030a 10309a 10208a 4500.0 0.016 * * 0.0 0
    1030b 10309b 10208b 4500.0 0.016 * * 0.0 0
    1030c 10309c 10208c 4500.0 0.016 * * 0.0 0
    1030d 10309d 10208d 4500.0 0.016 * * 0.0 0
    1570 15009 16009 5000.0 0.0154 * * 0.0 0
    1570a 15009a 16009a 5000.0 0.0154 * * 0.0 0
    ControlLink 15009b 16009b 5000.0 0.0154 * * 0.0 0
    1570c 15009c 16009c 100 0.0154 * * 0.0 0
    1570d 15009d 16009d 5000.0 0.0154 * * 0.0 0
    1570e 15009e 16009e 5000.0 0.0154 * * 0.0 0
    1600 16009 16109 500.0 0.015 * * 0.0 0
    1600a 16009a 16109a 500.0 0.015 * * 0.0 0
    1600b 16009b 16109b 500.0 0.015 * * 0.0 0
    1600c 16009c 16109c 500.0 0.015 * * 0.0 0
    1600d 16009d 16109d 500.0 0.015 * * 0.0 0
    1600e 16009e 16109e 500.0 0.015 * * 0.0 0
    1602 82309 16109 5000.0 0.034 * * 0.0 0
    1602a 82309a 16109a 5000.0 0.034 * * 0.0 0
    1602b 82309b 16109b 5000.0 0.034 * * 0.0 0
    1602c 82309c 16109c 5000.0 0.034 * * 0.0 0
    1602d 82309d 16109d 5000.0 0.034 * * 0.0 0
    1602e WetWell 16109e 5000.0 0.034 * * 0.0 0
    1630 16009 10309 300.0 0.015 * * 0.0 0
    1630a 16009a 10309a 300.0 0.015 * * 0.0 0
    1630b 16009b 10309b 300.0 0.015 * * 0.0 0
    1630c 16009c 10309c 300.0 0.015 * * 0.0 0
    1630d 16009d 10309d 300.0 0.015 * * 0.0 0
    1630e 16009e 10309e 300.0 0.015 * * 0.0 0
    ;CONDUIT DATA - base extran example or example 1
    8040 80408 80608 1800.0 0.015 * * 0.0 0
    8040a 80408a 80608a 1800.0 0.015 * * 0.0 0
    8040b 80408b 80608b 1800.0 0.015 * * 0.0 0
    8040c 80408c 80608c 1800.0 0.015 * * 0.0 0
    8040d 80408d 80608d 1800.0 0.015 * * 0.0 0
    8040e 80408e 80608e 1800.0 0.015 * * 0.0 0
    8060 80608 82309 2075.0 0.015 * 114.500 0.0 0
    8060a 80608a 82309a 2075.0 0.015 * 114.500 0.0 0
    8060b 80608b 82309b 2075.0 0.015 * 114.500 0.0 0
    8060c 80608c 82309c 2075.0 0.015 * 114.500 0.0 0
    8060d 80608d 82309d 2075.0 0.015 * 114.500 0.0 0
    8060e 80608e WetWell 2075.0 0.015 * 114.500 0.0 0
    8100 81009 81309 5100.0 0.015 * * 0.0 0
    8100a 81009a 81309a 5100.0 0.015 * * 0.0 0
    8100b 81009b 81309b 5100.0 0.015 * * 0.0 0
    8100c 81009c 81309c 5100.0 0.015 * * 0.0 0
    8100d 81009d 81309d 5100.0 0.015 * * 0.0 0
    8100e 81009e 81309e 5100.0 0.015 * * 0.0 0
    8130 81309 15009 3500.0 0.015 * * 0.0 0
    8130a 81309a 15009a 3500.0 0.015 * * 0.0 0
    8130b 81309b 15009b 3500.0 0.015 * * 0.0 0
    8130c 81309c 15009c 3500.0 0.015 * * 0.0 0
    8130d 81309d 15009d 3500.0 0.015 * * 0.0 0
    8130e 81309e 15009e 3500.0 0.015 * * 0.0 0
    [PUMPS]
    ;;Pump From Node To Node Pump Curve Status Sartup Shutoff
    ;* IPTYP NJUNC NJUNC PRATE1 - PRATE3 VRATE1 VRATE2 - for example 7
    Pump1 WetWell 15009e Pump1_Curve OFF 1 0
    Pump2 WetWell 15009e Pump1_Curve ON 2 1
    Pump3 WetWell 15009e Pump1_Curve ON 5 2.5
    [ORIFICES]
    ;;Orifice From Node To Node Type CrestHt Qcoeff Gated CloseTime
    ;* SIDE-OUTLET ORIFICE AT JUNCTION 82309d for the 5th network
    OR1@82309d-82308d 82309d 82308d SIDE * 0.85 NO 0
    ;* SUMP ORIFICE AT JUNCTION 82309b for the 3rd network
    ControlOrifice 82309b 15009b BOTTOM * 0.85 NO 0.25
    [WEIRS]
    ;;Weir From Node To Node Type CrestHt Qcoeff Gated EndCon EndCoeff Surcharge
    ;* TRANVERSE WEIR AT JUNCTION 82309c for the 4th network
    WEIR1@82309c-15009c 82309c 15009c TRANSVERSE 113 3.3 NO 0 0 YES
    [XSECTIONS]
    ;;Link Shape Geom1 Geom2 Geom3 Geom4 Barrels
    1030e TRIANGULAR 9.0 54.0 0 0 1.0
    1030 TRIANGULAR 9.0 54.0 0 0 1.0
    1030a TRIANGULAR 9.0 54.0 0 0 1.0
    1030b TRIANGULAR 9.0 54.0 0 0 1.0
    1030c TRIANGULAR 9.0 54.0 0 0 1.0
    1030d TRIANGULAR 9.0 54.0 0 0 1.0
    1570 CIRCULAR 5.5 0.0 0.0 0.0 1.0
    1570a CIRCULAR 5.5 0.0 0.0 0.0 1.0
    ControlLink CIRCULAR 5.5 0.0 0.0 0.0 1.0
    1570c CIRCULAR 5.5 0.0 0.0 0.0 1.0
    1570d CIRCULAR 5.5 0.0 0.0 0.0 1.0
    1570e CIRCULAR 5.5 0.0 0.0 0.0 1.0
    1600 CIRCULAR 6.0 0.0 0.0 0.0 1.0
    1600a CIRCULAR 6.0 0.0 0.0 0.0 1.0
    1600b CIRCULAR 6.0 0.0 0.0 0.0 1.0
    1600c CIRCULAR 6.0 0.0 0.0 0.0 1.0
    1600d CIRCULAR 6.0 0.0 0.0 0.0 1.0
    1600e CIRCULAR 6.0 0.0 0.0 0.0 1.0
    1602 CIRCULAR 5.0 0.0 0.0 0.0 1.0
    1602a CIRCULAR 5.0 0.0 0.0 0.0 1.0
    1602b CIRCULAR 5.0 0.0 0.0 0.0 1.0
    1602c CIRCULAR 5.0 0.0 0.0 0.0 1.0
    1602d CIRCULAR 5.0 0.0 0.0 0.0 1.0
    1602e CIRCULAR 5.0 0.0 0.0 0.0 1.0
    1630 TRIANGULAR 9.0 54.0 0 0 1.0
    1630a TRIANGULAR 9.0 54.0 0 0 1.0
    1630b TRIANGULAR 9.0 54.0 0 0 1.0
    1630c TRIANGULAR 9.0 54.0 0 0 1.0
    1630d TRIANGULAR 9.0 54.0 0 0 1.0
    1630e TRIANGULAR 9.0 54.0 0 0 1.0
    8040 FORCE_MAIN 4.0 122 0 0 1 1
    8040a CIRCULAR 4.0 0.0 0.0 0.0 1.0
    8040b CIRCULAR 4.0 0.0 0.0 0.0 1.0
    8040c CIRCULAR 4.0 0.0 0.0 0.0 1.0
    8040d CIRCULAR 4.0 0.0 0.0 0.0 1.0
    8040e CIRCULAR 4.0 0.0 0.0 0.0 1.0
    8060 CIRCULAR 4.0 0.0 0.0 0.0 1.0
    8060a CIRCULAR 4.0 0.0 0.0 0.0 1.0
    8060b CIRCULAR 4.0 0.0 0.0 0.0 1.0
    8060c CIRCULAR 4.0 0.0 0.0 0.0 1.0
    8060d CIRCULAR 4.0 0.0 0.0 0.0 1.0
    8060e CIRCULAR 4.0 0.0 0.0 0.0 1.0
    8100 CIRCULAR 4.5 0.0 0.0 0.0 1.0
    8100a CIRCULAR 4.5 0.0 0.0 0.0 1.0
    8100b CIRCULAR 4.5 0.0 0.0 0.0 1.0
    8100c CIRCULAR 4.5 0.0 0.0 0.0 1.0
    8100d CIRCULAR 4.5 0.0 0.0 0.0 1.0
    8100e CIRCULAR 4.5 0.0 0.0 0.0 1.0
    8130 CIRCULAR 4.5 0.0 0.0 0.0 1.0
    8130a CIRCULAR 4.5 0.0 0.0 0.0 1.0
    8130b CIRCULAR 4.5 0.0 0.0 0.0 1.0
    8130c CIRCULAR 4.5 0.0 0.0 0.0 1.0
    8130d CIRCULAR 4.5 0.0 0.0 0.0 1.0
    8130e CIRCULAR 4.5 0.0 0.0 0.0 1.0
    OR1@82309d-82308d CIRCULAR 2 0 0 0
    ControlOrifice CIRCULAR 1 0 0 0
    WEIR1@82309c-15009c RECT_OPEN 6 3 0 0
    [LOSSES]
    ;;Link Kinlet Koutlet Kavg Flap Gate SeepRate
    8040 0 0 1 NO 0
    [CONTROLS]
    ;;Control Rules
    Rule Downstream
    IF SIMULATION CLOCKTIME = 0:30:00
    OR SIMULATION CLOCKTIME = 1:30:00
    OR SIMULATION CLOCKTIME = 2:30:00
    OR SIMULATION CLOCKTIME = 3:30:00
    OR SIMULATION CLOCKTIME = 4:30:00
    OR SIMULATION CLOCKTIME = 5:30:00
    OR SIMULATION CLOCKTIME = 6:30:00
    OR SIMULATION CLOCKTIME = 7:30:00
    OR SIMULATION CLOCKTIME = 8:30:00
    OR SIMULATION CLOCKTIME = 9:30:00
    OR SIMULATION CLOCKTIME = 10:30:00
    OR SIMULATION CLOCKTIME = 11:30:00
    OR SIMULATION CLOCKTIME = 12:30:00
    OR SIMULATION CLOCKTIME = 13:30:00
    OR SIMULATION CLOCKTIME = 14:30:00
    OR SIMULATION CLOCKTIME = 15:30:00
    OR SIMULATION CLOCKTIME = 16:30:00
    OR SIMULATION CLOCKTIME = 17:30:00
    OR SIMULATION CLOCKTIME = 18:30:00
    OR SIMULATION CLOCKTIME = 19:30:00
    OR SIMULATION CLOCKTIME = 20:30:00
    OR SIMULATION CLOCKTIME = 21:30:00
    OR SIMULATION CLOCKTIME = 22:30:00
    OR SIMULATION CLOCKTIME = 23:30:00
    AND Link ControlLink Flow > 10
    Then Orifice ControlOrifice Setting = 0.0
    ELSE Orifice ControlOrifice Setting = 1.0
    [INFLOWS]
    ;;Node Inflow Time Series Type Funits Fscale Baseline Pattern
    80408 FLOW INFLOW@80408 FLOW 1.0 1.0 1
    80408a FLOW INFLOW@80408a FLOW 1.0 1.0
    80408b FLOW INFLOW@80408b FLOW 1.0 1.0
    80408c FLOW INFLOW@80408c FLOW 1.0 1.0
    80408d FLOW INFLOW@80408d FLOW 1.0 1.0
    80408e FLOW INFLOW@80408e FLOW 1.0 0.25
    81009 FLOW INFLOW@81009 FLOW 1.0 1.0
    81009a FLOW INFLOW@81009a FLOW 1.0 1.0
    81009b FLOW INFLOW@81009b FLOW 1.0 1.0
    81009c FLOW INFLOW@81009c FLOW 1.0 1.0
    81009d FLOW INFLOW@81009d FLOW 1.0 1.0
    81009e FLOW INFLOW@81009e FLOW 1.0 1.0
    82309 FLOW INFLOW@82309 FLOW 1.0 1.0
    82309a FLOW INFLOW@82309a FLOW 1.0 1.0
    82309b FLOW INFLOW@82309b FLOW 1.0 1.0
    82309c FLOW INFLOW@82309c FLOW 1.0 1.0
    WetWell FLOW INFLOW@82309e FLOW 1.0 1.0
    82309d FLOW INFLOW@82309d FLOW 1.0 1.0
    [DWF]
    ;;Node Parameter BaseDWF Patterns
    16109 FLOW 0.0
    80408 FLOW 10 "30_Minute"
    80408a FLOW 10 "30_Minute"
    [CURVES]
    ;;Curve Type X-Value Y-Value
    Pump2_Curve Pump3 1 10
    Pump2_Curve 2 8
    Pump2_Curve 3 6
    Pump2_Curve 4 4
    Pump2_Curve 5 2
    Pump2_Curve 6 2
    Pump2_Curve 7 2
    Pump2_Curve 8 2
    Pump2_Curve 9 2
    Pump2_Curve 10 2
    Pump1_Curve Pump3 1 5
    Pump1_Curve 2 4
    Pump1_Curve 3 3
    Pump1_Curve 4 2
    Pump1_Curve 5 1
    Pump1_Curve 6 1
    Pump1_Curve 7 1
    Pump1_Curve 8 1
    Pump1_Curve 9 1
    Pump1_Curve 10 1
    Pump3_Curve Pump3 1 15
    Pump3_Curve 2 12
    Pump3_Curve 3 9
    Pump3_Curve 4 6
    Pump3_Curve 5 3
    Pump3_Curve 6 3
    Pump3_Curve 7 3
    Pump3_Curve 8 3
    Pump3_Curve 9 3
    Pump3_Curve 10 3
    SB1 Storage 0 0
    SB1 1 0
    SB1 1.5 0
    SB1 2 0
    SB1 2.5 340
    SB1 3 2483
    SB1 3.5 5686
    SB1 4 11585
    SB1 4.5 51299
    SB1 5 278327
    SB1 5.5 526214
    SB1 6 740422
    SB1 6.5 839055
    SB1 7 864692
    SB1 8 866863
    SB1 9 868103
    SB1 10 868394
    SB2 Storage 0 0
    SB2 1 0
    SB2 1.5 7103
    SB2 2 31791
    SB2 2.5 71923
    SB2 3 122585
    SB2 3.5 183836
    SB2 4 272757
    SB2 4.5 460705
    SB2 5 751151
    SB2 5.5 967995
    SB2 6 1095621
    SB2 6.5 1101547
    SB2 7 1101970
    SB2 8 1102600
    SB2 9 1103111
    SB2 10 1103519
    SB3 Storage 0 0
    SB3 1 0
    SB3 1.5 0
    SB3 2 0
    SB3 2.5 0
    SB3 3 332
    SB3 3.5 23187
    SB3 4 127395
    SB3 4.5 316178
    SB3 5 471158
    SB3 5.5 554586
    SB3 6 598930
    SB3 6.5 615368
    SB3 7 619054
    SB3 8 623164
    SB3 9 626320
    SB3 10 628073
    SB4 Storage 0 1565
    SB4 1 2261
    SB4 1.5 2607
    SB4 2 3010
    SB4 2.5 3441
    SB4 3 3901
    SB4 3.5 4388
    SB4 4 6141
    SB4 4.5 73936
    SB4 5 305776
    SB4 5.5 477898
    SB4 6 581768
    SB4 6.5 602558
    SB4 7 605744
    SB4 8 606120
    SB4 9 606441
    SB4 10 606768
    SB5 Storage 0 0
    SB5 1 0
    SB5 1.5 0
    SB5 2 0
    SB5 2.5 39
    SB5 3 7520
    SB5 3.5 45065
    SB5 4 83112
    SB5 4.5 161541
    SB5 5 235404
    SB5 5.5 295242
    SB5 6 322603
    SB5 6.5 341396
    SB5 7 347583
    SB5 8 355460
    SB5 9 358876
    SB5 10 359746
    SB6 Storage 0 0
    SB6 1 28
    SB6 1.5 62
    SB6 2 111
    SB6 2.5 174
    SB6 3 671
    SB6 3.5 20637
    SB6 4 115442
    SB6 4.5 280562
    SB6 5 438832
    SB6 5.5 604771
    SB6 6 711883
    SB6 6.5 754132
    SB6 7 772875
    SB6 8 777041
    SB6 9 777041
    SB6 10 777041
    SB7 Storage 0 0
    SB7 1 76
    SB7 1.5 161
    SB7 2 277
    SB7 2.5 425
    SB7 3 604
    SB7 3.5 814
    SB7 4 1094
    SB7 4.5 13105
    SB7 5 92154
    SB7 5.5 244856
    SB7 6 425764
    SB7 6.5 534327
    SB7 7 603342
    SB7 8 629626
    SB7 9 635380
    SB7 10 639804
    SB8 Storage 0 0
    SB8 1 0
    SB8 1.5 0
    SB8 2 0
    SB8 2.5 3210
    SB8 3 18142
    SB8 3.5 39310
    SB8 4 66507
    SB8 4.5 121586
    SB8 5 199685
    SB8 5.5 318789
    SB8 6 434905
    SB8 6.5 529773
    SB8 7 610618
    SB8 8 692084
    SB8 9 742023
    SB8 10 766289
    SB9 Storage 0 0
    SB9 1 0
    SB9 1.5 0
    SB9 2 0
    SB9 2.5 0
    SB9 3 0
    SB9 3.5 0
    SB9 4 0
    SB9 4.5 2
    SB9 5 2361
    SB9 5.5 49440
    SB9 6 264589
    SB9 6.5 600759
    SB9 7 986301
    SB9 8 1176915
    SB9 9 1187853
    SB9 10 1189988
    [TIMESERIES]
    ;;Time Series Date Time Value
    INFLOW@82309 01/01/1988 00:00 0.00000
    INFLOW@82309 00:15 40.00000
    INFLOW@82309 03:00 40.00000
    INFLOW@82309 03:15 0.00000
    INFLOW@82309 12:00 0.00000
    INFLOW@80408 01/01/1988 00:00 0.00000
    INFLOW@80408 00:15 45.00000
    INFLOW@80408 03:00 45.00000
    INFLOW@80408 03:15 0
    INFLOW@80408 12:00 0
    INFLOW@80408 01/11/1988 0:00 0
    INFLOW@81009 01/01/1988 00:00 0.00000
    INFLOW@81009 00:15 50.00000
    INFLOW@81009 03:00 50.00000
    INFLOW@81009 03:15 0.00000
    INFLOW@81009 12:00 0.00000
    INFLOW@82309a 01/01/1988 00:00 0.00000
    INFLOW@82309a 00:15 40.00000
    INFLOW@82309a 03:00 40.00000
    INFLOW@82309a 03:15 0.00000
    INFLOW@82309a 12:00 0.00000
    INFLOW@80408a 01/01/1988 00:00 0.00000
    INFLOW@80408a 00:15 45.00000
    INFLOW@80408a 03:00 45.00000
    INFLOW@80408a 03:15 0.00000
    INFLOW@80408a 12:00 0.00000
    INFLOW@81009a 01/01/1988 00:00 0.00000
    INFLOW@81009a 00:15 50.00000
    INFLOW@81009a 03:00 50.00000
    INFLOW@81009a 03:15 0.00000
    INFLOW@81009a 12:00 0.00000
    INFLOW@82309b 01/01/1988 00:00 0.00000
    INFLOW@82309b 00:15 40.00000
    INFLOW@82309b 03:00 40.00000
    INFLOW@82309b 03:15 0.00000
    INFLOW@82309b 12:00 0.00000
    INFLOW@80408b 01/01/1988 00:00 0.00000
    INFLOW@80408b 00:15 45.00000
    INFLOW@80408b 03:00 45.00000
    INFLOW@80408b 03:15 0.00000
    INFLOW@80408b 12:00 0.00000
    INFLOW@81009b 01/01/1988 00:00 0.00000
    INFLOW@81009b 00:15 50.00000
    INFLOW@81009b 03:00 50.00000
    INFLOW@81009b 03:15 0.00000
    INFLOW@81009b 12:00 0.00000
    INFLOW@82309c 01/01/1988 00:00 0.00000
    INFLOW@82309c 00:15 40.00000
    INFLOW@82309c 03:00 40.00000
    INFLOW@82309c 03:15 0.00000
    INFLOW@82309c 12:00 0.00000
    INFLOW@80408c 01/01/1988 00:00 0.00000
    INFLOW@80408c 00:15 45.00000
    INFLOW@80408c 03:00 45.00000
    INFLOW@80408c 03:15 0.00000
    INFLOW@80408c 12:00 0.00000
    INFLOW@81009c 01/01/1988 00:00 0.00000
    INFLOW@81009c 00:15 50.00000
    INFLOW@81009c 03:00 50.00000
    INFLOW@81009c 03:15 0.00000
    INFLOW@81009c 12:00 0.00000
    INFLOW@82309d 01/01/1988 00:00 0.00000
    INFLOW@82309d 00:15 40.00000
    INFLOW@82309d 03:00 40.00000
    INFLOW@82309d 03:15 0.00000
    INFLOW@82309d 12:00 0.00000
    INFLOW@80408d 01/01/1988 00:00 0.00000
    INFLOW@80408d 00:15 45.00000
    INFLOW@80408d 03:00 45.00000
    INFLOW@80408d 03:15 0.00000
    INFLOW@80408d 12:00 0.00000
    INFLOW@81009d 01/01/1988 00:00 0.00000
    INFLOW@81009d 00:15 50.00000
    INFLOW@81009d 03:00 50.00000
    INFLOW@81009d 03:15 0.00000
    INFLOW@81009d 12:00 0.00000
    INFLOW@82309e 01/01/1988 00:00 0.00000
    INFLOW@82309e 00:15 40.00000
    INFLOW@82309e 03:00 40.00000
    INFLOW@82309e 03:15 0.00000
    INFLOW@82309e 12:00 0.00000
    INFLOW@80408e 01/01/1988 00:00 0.00000
    INFLOW@80408e 00:15 45.00000
    INFLOW@80408e 03:00 45.00000
    INFLOW@80408e 03:15 0.00000
    INFLOW@80408e 12:00 0.00000
    INFLOW@81009e 01/01/1988 00:00 0.00000
    INFLOW@81009e 00:15 50.00000
    INFLOW@81009e 03:00 50.00000
    INFLOW@81009e 03:15 0.00000
    INFLOW@81009e 12:00 0.00000
    OpenOrifice 0:00 0
    OpenOrifice 1:00 0
    OpenOrifice 1:05 0.1
    OpenOrifice 1:10 0.2
    OpenOrifice 1:15 0.5
    OpenOrifice 1:30 1
    OpenOrifice 11:00 1
    [PATTERNS]
    ;;Pattern Type Multipliers
    30_Minute MONTHLY 2 1.0 2 1.0 2 1.0
    30_Minute 2 1.0 2 1.0 2 1.0
    ;;Reporting Options
    INPUT NO
    CONTROLS YES
    SUBCATCHMENTS ALL
    NODES ALL
    LINKS ALL
    [TAGS]
    Node 10309 10309
    Node 10309a 10309a
    Node 10309b 10309b
    Node 10309c 10309c
    Node 10309d 10309d
    Node 10309e 10309e
    Node 15009 15009
    Node 15009a 15009a
    Node 15009b 15009b
    Node 15009c 15009c
    Node 15009d 15009d
    Node 15009e 15009e
    Node 16009 16009
    Node 16009a 16009a
    Node 16009b 16009b
    Node 16009c 16009c
    Node 16009d 16009d
    Node 16009e 16009e
    Node 16109 16109
    Node 16109a 16109a
    Node 16109b 16109b
    Node 16109c 16109c
    Node 16109d 16109d
    Node 16109e 16109e
    Node 80408 80408
    Node 80408a 80408a
    Node 80408b 80408b
    Node 80408c 80408c
    Node 80408d 80408d
    Node 80408e 80408e
    Node 80608 80608
    Node 80608a 80608a
    Node 80608b 80608b
    Node 80608c 80608c
    Node 80608d 80608d
    Node 80608e 80608e
    Node 81009 81009
    Node 81009a 81009a
    Node 81009b 81009b
    Node 81009c 81009c
    Node 81009d 81009d
    Node 81009e 81009e
    Node 81309 81309
    Node 81309a 81309a
    Node 81309b 81309b
    Node 81309c 81309c
    Node 81309d 81309d
    Node 81309e 81309e
    Node 82308d 82308d
    Node 82309 82309
    Node 82309a 82309a
    Node 82309b 82309b
    Node 82309c 82309c
    Node WetWell 82309e
    Node 10208 10208
    Node 10208b 10208b
    Node 10208c 10208c
    Node 10208d 10208d
    Node 10208e 10208e
    Node 10208a 10208a
    Node 82309d 82309d
    Link 1030e 1030e
    Link 1030 1030
    Link 1030a 1030a
    Link 1030b 1030b
    Link 1030c 1030c
    Link 1030d 1030d
    Link 1570 1570
    Link 1570a 1570a
    Link ControlLink 1570b
    Link 1570c 1570c
    Link 1570d 1570d
    Link 1570e 1570e
    Link 1600 1600
    Link 1600a 1600a
    Link 1600b 1600b
    Link 1600c 1600c
    Link 1600d 1600d
    Link 1600e 1600e
    Link 1602 1602
    Link 1602a 1602a
    Link 1602b 1602b
    Link 1602c 1602c
    Link 1602d 1602d
    Link 1602e 1602e
    Link 1630 1630
    Link 1630a 1630a
    Link 1630b 1630b
    Link 1630c 1630c
    Link 1630d 1630d
    Link 1630e 1630e
    Link 8040 8040
    Link 8040a 8040a
    Link 8040b 8040b
    Link 8040c 8040c
    Link 8040d 8040d
    Link 8040e 8040e
    Link 8060 8060
    Link 8060a 8060a
    Link 8060b 8060b
    Link 8060c 8060c
    Link 8060d 8060d
    Link 8060e 8060e
    Link 8100 8100
    Link 8100a 8100a
    Link 8100b 8100b
    Link 8100c 8100c
    Link 8100d 8100d
    Link 8100e 8100e
    Link 8130 8130
    Link 8130a 8130a
    Link 8130b 8130b
    Link 8130c 8130c
    Link 8130d 8130d
    Link 8130e 8130e
    [MAP]
    DIMENSIONS -1663.687 1565.261 22200.527 20392.630
    Units None
    [COORDINATES]
    ;;Node X-Coord Y-Coord
    10309 389.470 2421.050
    10309a 389.470 8421.050
    10309b 389.470 14421.050
    10309c 11389.470 14421.050
    10309d 11389.470 8421.050
    10309e 11389.470 2421.050
    15009 4978.950 2421.050
    15009a 4978.950 8421.050
    15009b 4978.950 14421.050
    15009c 15978.950 14421.050
    15009d 15978.950 8421.050
    15009e 15989.044 2458.354
    16009 2494.740 2421.050
    16009a 2494.740 8421.050
    16009b 2494.740 14421.050
    16009c 13494.740 14421.050
    16009d 13494.740 8421.050
    16009e 13494.740 2421.050
    16109 2494.740 7536.840
    16109a 2494.740 13536.840
    16109b 2494.740 19536.840
    16109c 13494.740 19536.840
    16109d 13494.740 13536.840
    16109e 13494.740 7536.840
    80408 10115.790 7536.840
    80408a 10115.790 13536.840
    80408b 10115.790 19536.840
    80408c 21115.790 19536.840
    80408d 21115.790 13536.840
    80408e 21115.790 7536.840
    80608 7463.160 7536.840
    80608a 7463.160 13536.840
    80608b 7463.160 19536.840
    80608c 18463.160 19536.840
    80608d 18463.160 13536.840
    80608e 18463.160 7536.840
    81009 9989.470 2421.050
    81009a 9989.470 8421.050
    81009b 9989.470 14421.050
    81009c 20989.470 14421.050
    81009d 20989.470 8421.050
    81009e 20989.470 2421.050
    81309 7568.420 2421.050
    81309a 7568.420 8421.050
    81309b 7568.420 14421.050
    81309c 18568.420 14421.050
    81309d 18568.420 8421.050
    81309e 18568.420 2421.050
    82308d 14957.890 13536.840
    82309 4957.890 7536.840
    82309a 4957.890 13536.840
    82309b 4957.890 19536.840
    82309c 15957.890 19536.840
    WetWell 15989.044 7551.399
    10208 -578.950 4947.370
    10208b -578.950 16947.370
    10208c 10420.950 16947.370
    10208d 10420.950 10947.370
    10208e 10420.950 4947.370
    10208a -578.950 10947.370
    82309d 15957.890 13536.840
    [VERTICES]
    ;;Link X-Coord Y-Coord
    Pump2 17184.407 5903.447
    Pump3 14939.544 5894.780
    [LABELS]
    ;;X-Coord Y-Coord Label
    7150.770 5209.268 "#1" "" "Arial" 10 0 0
    6948.325 11444.569 "#2" "" "Arial" 10 0 0
    6664.902 17436.936 "#3" "" "Arial" 10 0 0
    18568.658 17679.869 "#4" "" "Arial" 10 0 0
    18568.658 11444.569 "#5" "" "Arial" 10 0 0
    18690.125 5492.691 "#6" "" "Arial" 10 0 0
    [PROFILES]
    ;;Name Links
    "profileA " 8040 8060 1602
  • A rule like this may work
    Rule Downstream
    See also my example which may help you
    • Thanks Robert for the example. But what will happen , say at 0:31, wouldn't the setting of the orifice be changed again to 1.0, even if the FLOW in the link is greater than 10?